 Sewer Line Question

View previous topic View next topic Go down 
AuthorMessage
jacbson



Posts : 2
Join date : 2008-08-01

PostSubject: Sewer Line Question   Fri Aug 01, 2008 4:44 pm

What would be the best way to handle this? We are realigning an existing 36" RCP sewer line that currently has about 2' of cover. The new sewer will need to be installed beneath an access road that frequently has loading trucks.

Would it be better to just use a reinforced concrete jacket around the pipe or use a higher class of concrete pipe? How much more strength does a jacket provide?

jack
Back to top Go down
View user profile
Admin
Admin


Posts : 7
Join date : 2008-07-17

PostSubject: Re: Sewer Line Question   Fri Aug 01, 2008 4:47 pm

Back fill with lean concrete, (including one foot above and below), makes a thick concrete pipe capable of enormous loads.
Back to top Go down
View user profile http://fdccorporationforum.fdccorporation.comforumotionforum.fdc
nickhernandez



Posts : 4
Join date : 2008-07-21

PostSubject: Re: Sewer Line Question   Fri Aug 01, 2008 4:48 pm

Couple of questions come to mind. First, the 2' of cover, is that top of pipe to finished concrete, or TP to begining of subgrade? Also, are you planning on re-using the 36" concrete pipe or replacing it? Also what kind of surface above the pipe, is is HMAC or reinforced concrete?

I would follow gbam's suggestion of determining loads, maybe an H-20 loading situation or more. Second, the pipe manufacturers tend to be very helpful with this. They will have real world tests of pipe load capacity. You can use a higher class RCP (make it poly lined too, if it is wastewater application, hydrogen sulfides in ww are known to erode concrete)

My guess is you can find a new pipe that can handle the loads without going to special jacket. Probably be less expensive to install too, rather than re-use of old pipe (which may be old and deteriorated) with some form of jacket around it.
Back to top Go down
View user profile
jacbson



Posts : 2
Join date : 2008-08-01

PostSubject: Re: Sewer Line Question   Fri Aug 01, 2008 4:50 pm

To answer some of your questions, a new 36" pipe will be installed with PVC liner to resist corrosion. The 2' cover is measured from the top of pavement to the top of pipe so that includes the pavement thickness, subgrade, and backfill (thicknesses yet to be determined).

My initial discussions with the manufacturers is that we can get by with 1' of minimum cover over standard class 3 RCP. I'm hesitant mainly because the acceptable standard is to provide at least 4' of cover. So if we install it at a shallower depth and run into any problems, we're at risk for deviating from the standard.

Thanks again for the options... definitely food for thought.
Back to top Go down
View user profile
morales



Posts : 1
Join date : 2008-08-01

PostSubject: Re: Sewer Line Question   Fri Aug 01, 2008 4:52 pm

The class of pipe you need is going to be determined by the loading on the pipe (live and dead), the type of installation, and existing soil conditions. The American Concrete Pipe Association puts out a free design manual that includes load calculation and pipe strength requirements. It also includes design examples. This is the link to the design manual http://www.concrete-pipe.org/designmanual.htm.

I'm going to assume you have access to information on the existing soil types at the site. Now the pipe is crossed by access road so you need to determine the loading. HS-20 is a standard load and should be fine unless you have evidence of larger trucks using the road. Next select a type of bedding based on the soil information and determine the D-load on the pipe. Then select a class of pipe that meets that load.

There are some excelent examples in the design manual. As gbam said it will likely be cheaper and easier to install a higher class of pipe rather than constuct a concrete cap. I've seen loaded twin axle dump trucks drive over class 5 rcp with 6-inches of cover with no ill effects on the pipe and Class 3 RCP will likely be sufficient but as stated before just run through the design calcs to make sure.

One thing to remember is if you specifiy a higher class of bedding you can use a lower strength pipe, but you'll have to have tighter controls on installation to make sure it is constructed correctly. Its usually better to assume a lower bedding class for design purposes as it will result in a more conservative design and account for any installation errors.
Back to top Go down
View user profile
Sponsored content




PostSubject: Re: Sewer Line Question   

Back to top Go down
 
Sewer Line Question
View previous topic View next topic Back to top 
Page 1 of 1
 Similar topics
-
» Monstrous creatures, vehicles and Line of Sight
» More a Query: Fighting Sewer Monsters
» Red Line Racers
» Chaos Icon Line Study
» Question about Carapace Sword

Permissions in this forum:You cannot reply to topics in this forum
FDC & Associates Community Forum :: FDC Customer-Engineering Connection :: General Questions and Communication-
Jump to: